50amp vs 30am hookup question
  • 29 Replies
  • 39883 Views
Re: 50amp vs 30am hookup question
« Reply #15 on: July 05, 2021, 11:23:46 am »
Volkemon:
Might want to consider some overcurrent protection for the two GFI's.
I know the 30 amp receptacles on a 50 amp circuit is done all the time (though I don't know why it is allowed) but up to 50 amps on a 120volt extension cord could present a danger.
Probably the easiest way to make it safer would be to stick an inline fuse ahead of the GFIs.
Just my 2 cents.
Hm!  The few parks that we have seen with 50,30 and 20A duplex have all had separate breakers of the appropriate value to control each one. I agree, in a commercial install I would wonder how 50A breaker on a 30A rated service is allowed.
The box isnt in a 'free public use' situation. Should we be using it like that. I would CERTAINLY have it fuse/breaker protected. I agree with the safety concerns you raise. If I can find some 'push button' reset breakers that would fit in the limited free area I have in the box, they might be added.
The box is used outside, and at the base of the post. Placed ~6 feet away from it, and away from any other objects that can be damaged if it 'blows'.  Should any of the 'tenters' that use the duplex outlets try to pull 50A , their extension cords will become heater elements then ground display sparklers.  :lol The 10Ga solid wire in the box will last longer.  Might even take out the duplex outlet. Either way, my camper and trailer will be fine.  2o2
Yes, there are 10Ga extension cords, I have one. But the folks that use those outlets have 16 or 14GA cords as a rule. Maybe 12ga, but generally just smaller ones to run fans and cellphone chargers.  And they are cognizant of the limited power use they have, not even hotplates or coffee makers allowed. We have a communal kitchen for that. In a festival environment, tenters around us are generally friends of ours, and VERY grateful to have any power. 'Abuse it and lose it' is the rule. You do NOT want to be tenting in Florida in July with no fan, so the rules are respected.
Worst case, should someone come in the dead of night, plug in their shore power cord with an adapter, and run it to their camper and try to fire up both A/C's and the microwave.... My bet is that the GFCI outlet will fail. They will be on a GFCI, as I am using both 30A for the camper and the cycle hauler. Should the A/C in the camper or trailer stop, believe you me, the occupants will be up and about quickly to see what happened.  >(
jim.godfrey
  • 292
  • PurchDate: October 2019
« Reply #16 on: July 05, 2021, 01:58:05 pm »
I agree the likelihood of one of the tenters  trying to draw that much power is slim but...
Something like this would be cheap and easy insurance.
https://smile.amazon.com/RKURCK-Thermal-Breakers-Overload-Protector/dp/B081PR343M/ref=sr_1_13?dchild=1&keywords=20+amp+120+volt+panel+mounted+fuse&qid=1625497534&sr=8-13
« Reply #17 on: July 05, 2021, 02:48:14 pm »
Very true. Is my wife messaging you!    roflol
And now that I have laughed at it, better get them before the box catches on fire at the next festy.  (exactly)
Thanks for the link!   :)(:  In the cart.
GA Steve
  • 14
  • PurchDate: Looking for 2552
« Reply #18 on: July 07, 2021, 11:34:38 am »
I bought a Cable Matters 50 Amp to 30 Amp RV Adapter Splitter from Amazon that I had researched.   I did not find out in any comments on Amazon or from the CM website itself how it was wired.  Upon receiving the product I tested using continuity on a meter to see if hot leg 1 went to one 30 amp and hot let 2 went to the other 30 amp which is the way Volkemon wired his.  My finding was that it did not.  BOTH 30 amp receptacles were from hot leg 1. So I am assuming all like splitters will be the same as the one from Amazon.  Returned.  It looked like a quality product but not worth busting into.
https://www.amazon.com/gp/product/B07WTXWXGB/ref=ppx_yo_dt_b_asin_title_o03_s00?ie=UTF8&psc=1
« Reply #19 on: July 07, 2021, 02:36:26 pm »
I agree totally with Donc13.
I have made a 50 to 30 adapter using the OTHER leg of the 120.  Although I have not had experience with this, I understand that if the campground is nearly full and 'on the edge' of low voltage - and the 50 amp is available you may have better luck with the locked rotor voltage drop on initial A.C. startup.
DonC13 comments?
And I LOVE Volkemon's Craftsman box setup.  I need to make one of those!!  Volkemon, do you have a picture of the underside?  I assume you use different hot legs for each 30 amp plug connection.  I can wire it if you don't.
Steve
Yes, in a low voltage situation (say 105v AC or lower) you can easily blow the breaker due to A/C compressor 'hard start'. And that's exactly why I added a SoftStartRV to my A/C unit.  It reduces startup current for the compressor from 52amp (for 1/2 second) to 24amp (for 1 second).  Both are in the normal 'time delay' range for a circuit breaker.  But lowering the voltage by 10% (from 120v to 108v = 10% voltage drop) also means a 10% raise in the amperage to maintain the same 'power' and that 52 amp surge will jump to almost 60 amps and pop the breaker.
« Reply #20 on: July 07, 2021, 04:17:41 pm »
Wow!  I would have thought the same. It does state in the questions and review that it does not, however. I feel a little better about my setup not having fuses...check out this wonder..
https://www.amazon.com/dp/B08NXHHCKG
""10 AWG all-copper wires,""
So no fuses/ breakers, and it will roast all the way back to the 50A plug.  :lol  at least they use both legs.  2o2   It may look hokey, but I like my little 'Powerbox' more and more.
GA Steve
  • 14
« Reply #21 on: July 07, 2021, 05:22:28 pm »
"Wow!  I would have thought the same. It does state in the questions and review that it does not, however. I feel a little better about my setup not having fuses...check out this wonder..
https://www.amazon.com/dp/B08NXHHCKG"
I had ordered that Cable Matters plug BEFORE that Q&A post about it only using one hot leg (Black).  I just saw that comment today.
However,
Volkemon, your "wonder" 50 to 20 posted above is the first commercial one using both hot legs.  Just a few bucks more ($8), but you can CLEARLY see the hot leg #1 Black and the hot leg #2 Red thru the resin composite.  You can also see the common White bus that connects all the 20 amp receptacles.  Very cool find!
"So no fuses/ breakers, and it will roast all the way back to the 50A plug."  Where do you see the weak point in this.  Are you thinking there may be an internal short in the clear resin, or are you thinking someone may try drawing many amps thru one 20amp plug?
I agree Volkemon, your 30amp setup does look safer....
However, here is another choice that at least one reviewer claims it does use both legs.  This one is by LeisureCord store. I guess the only way to know is to order one (as I had done above) and check it with a voltmeter to see...
https://www.amazon.com/gp/product/B079NL42ZS/ref=ox_sc_act_title_1?smid=AIVNKK5E0ABND&psc=1
« Last Edit: July 07, 2021, 06:15:45 pm by GA Steve »
« Reply #22 on: July 07, 2021, 07:02:10 pm »
All 50a male to 30a female only use one leg of the 50a circuit.  Remember, L1 and L2 are each 120v BUT 180 degrees out of phase, so crossing those 2 will be 240v and a huge electric arc!
« Reply #23 on: July 07, 2021, 07:28:18 pm »
TRUE....but we are addressing getting (2) 30A female connections out of (1) 50A female receptacle.
The adapter that would APPEAR to do that only uses one leg, and could have used both. Disappointing.
The adapter even says its 'Rated' to 7200 watts like that's what it gives you... when it can only draw 6000w through one leg.  >(
Its pretty easy to get (2) 30A females out of one 50A male without sparks. GA Steve just posted a link to one that (hopefully!) does. ( https://www.amazon.com/gp/product/B079NL42ZS ) I did the same in a 'redneck' manner with my box.
The latter. Not really a concerning point, however.
Jim Godfrey was correct in pointing out I SHOULD have the breakers before the duplex outlets. I was sorta using the wire as a 'last chance fuse'.
Note how the NEW adapter you found (  https://www.amazon.com/gp/product/B079NL42ZS  )  has 10Ga to the junction, then says it has 6Ga to the 50A plug. My box is the same way....the 10Ga wire inside should toast before the 6Ga does damage. So the damage is in the box. (NO testing to confirm, hope I never conduct one!  roflol )
The 50A to (4) 20A outlets says it is all 10Ga to the 50A plug. So the 'hot wire' doesnt stop in the junction (in the adapters case), or in the box (in my case) . It will fry all the way up to the plug.
Really not a substantial difference, more an observation. Again, not gonna test.  2o2   Just 'Bench Racing' as they say.  :)(:
jim.godfrey
  • 292
« Reply #24 on: July 09, 2021, 04:56:38 pm »
Becha won't find a UL label on this puppy!!!!
???What could go wrong??? ;)
GA Steve
  • 14
--- What I was looking for ---
« Reply #25 on: July 10, 2021, 05:54:34 pm »
""However, here is another choice that at least one Amazon reviewer claims it does use both legs.  This one is by LeisureCord store. I guess the only way to know is to order one (as I had done above) and check it with a voltmeter to see...
https://www.amazon.com/gp/product/B079NL42ZS/ref=ox_sc_act_title_1?smid=AIVNKK5E0ABND&psc=1  ""
My post above HAS been ordered and received.  I took a meter set on continuity and CONFIRMED Leg 1 goes to one 30 amp, and Leg 2 goes to the other 30 amp.  Donc13 states that crossing these 2 will be a huge mistake.  These separate 30 amp legs would be used to serve different circuits and would not be combined.
Leisue Cord in California confirmed by phone that Leg 1 did not serve both 30 amp splitters and thus I felt comfortable ordering it.  From observation, this cord looks well made and is worth the $40.
Volkemon's box suits his needs better as he has more options and standard 110 outlets which is a benefit.
I would like to test my hypothesis when 50 amps are available and I find low voltage on my meter while using the electrical post 30 amp outlet.  I don't want to damage my A.C. trying to run on 105 to 108 volts.  So I will see if Leg 2 of the 50amp provides higher voltage.
« Last Edit: July 10, 2021, 06:03:12 pm by GA Steve »
« Reply #26 on: July 10, 2021, 08:10:54 pm »
Yes, that is designed to provide 2,totally separate 110v 30a circuits.  You NEVER want to plug anything into both 30a plugs that has any chance connecting L1 to L2!
A typical RV park wiring system has 1/2 the 30a pedestal sockets wired to L1 and the other half wired to L2.
Just like your home wiring, 1/2 your circuit breakers are wired to L1 and the other half to L2.
GA Steve
  • 14
« Reply #27 on: July 10, 2021, 09:43:13 pm »
Thanks for your informative post DonC.  To confirm (from this amateur), if you were to use this in a house, for example, one side would have to only go to breakers wired to Leg 1, and one side could ONLY go to breakers wired to Leg 2.  As I understand it, since 1 & 2 are out of phase, a crossover connection down line could result in 220 volts to one side due to the neutral white wire being common to both legs carrying voltage  - thereby destroying whatever is connected.
Please elaborate on "out of phase" connections.  Thanks for your expertise!
« Last Edit: July 10, 2021, 10:12:11 pm by GA Steve »
« Reply #28 on: July 11, 2021, 02:23:06 pm »
Think about two 6v batteries wired in series... B1 negative is connected to B2 positive.  So if you measure the voltage from B1 positive to B2 negative, you get 12v. But B1 positive to B1 negative is only 6v.  That connection between B1 negative to B2 positive would be considered the neutral wire in an alternating current (AC) system.  You don't want to touch B1 positive to B2 negative because you'll get a big spark!
So its like a neutral.   :beg  Really?  So if you attach the connecting wire between the two 6V batteries in your camper to the system ground, just like A/C does at the breaker box, all will be well?  Please do this in a safe place should you not know the answer. And have a fuse in your test wire.
There are fundamental differences between A/C and DC, and that can make some comparisons difficult.( Like saying cars and trains both have wheels, and both turn corners, so they must steer somewhat similar.).
For anyone else: this borders on a dangerous bit of misinformation. That connector wire, UNLIKE a neutral, is NOT a good ground or current return. Never use it as such.  Ever wonder why electric golf carts DO NOT ground the battery pack to the frame? There is good reason.
well...you probably wont have two phases in your residential house power anyway...
In the link to Wikipedia, please note this critical line:
""Three-wire single-phase systems, with a single center-tapped transformer giving two live conductors, is a common distribution scheme for residential and small commercial buildings in North America. This arrangement is sometimes incorrectly referred to as "two phase".""
If you accidently 'swap' your hot and neutral in the 110V 30A RV receptacle wiring, the connection between the neutral and ground in the camper should trip the supply breaker to the outlet instantly on plugging it in. Maybe burn the plug and/or receptacle contacts a little too. But it errs on the side of safety.
 I can see a scenario where you could have a 50A, 4 lug outlet mis-wired. ESPECIALLY when 'upgrading' an existing 240V 50A 3 wire outlet to a 4 wire receptacle so you can use common adapters for your RV. On a 50A shore power cord, the neutral/ground connection inside should trip the outlet supply breaker. Again, with possible arcing and damage during insertion.  With the 'splitter' or adapter, it could give you a working camper, but 120V between the step outside and the ground below.  :help  Get a severe 'tingle' when touching a metal part on the camper while standing on the ground outside. Or worse.... 240V instead of 120V blowing up devices. AND a 'tingly' camper when touched.  >(
This thread has gotten into a potentially dangerous area, PLEASE... DO NOT TAKE THIS INFORMAL DISCUSSION AS QUALIFIED INSTRUCTION.  You are dealing with 'invisible' forces that can kill you or others with little or no warning.   Electrical code, and inspectors, are there to ensure your safety. The deaths and injuries of others before us has led to the code we have today. Dont join them by ignoring code.
« Reply #29 on: July 11, 2021, 04:14:19 pm »
I removed the posting
I was not ever suggesting you hook ground to the wire between the two batteries!
I was saying to measure the VOLTAGE between terminals.   I never suggested anything else.   I was simply comparing the concept.
But you are right, there may well be someone reading this who would try it for some reason or other.. So... Posting gone.
As to "real" vs "center tapped transformer". Every RESIDENTIAL power distribution center that I have tested (5 or so that I have owned over the years) with  a dual trace oscilloscope show L1 referenced to neutral and L2 referenced to neutral 180 degrees out of phase.
But yes, that is a result of the electrical properties of center tapped transformers and not a true independent, dual phase system.
Sorry for the scare!