Main Forum => General Discussion => Topic started by: fandj on December 04, 2017, 08:42:44 pm

Title: 15 Amp Service Connection
Post by: fandj on December 04, 2017, 08:42:44 pm
Many of the campgrounds we stay that have electrical service typically have 15 amp, 30 amp, and some have 50 amp outlets.  Our PC is wired for 30 amp so this is the pedestal outlet we typically use.  During the winter when we are using a 1500 watt portable heater, water heater on 110 volt power, and microwave on 110 volt we have to be careful to not run all three at the same time or we draw too much power.  I am thinking of installing a dedicated 110 volt ground fault outlet in the PC to connect the portable heater.  This dedicated outlet would be isolated from the rest of the PC power circuitry and it would connect with a separate 10-12 gauge power cord which would be connected to the campground 15 amp pedestal outlet.

Has anyone done anything similar?  What safety issues should I be aware of other than using properly sized wiring, outlet, and connectors to handle the 15 amp service.  Am I correct in thinking that campground outlets with 15 amp and 30 amp service are capable of supplying a total of 45 amps or would they typically be protected at a maximum of 30 amps?

If I can get comfortable that this is safe and indeed will provide me the ability to run the portable heater while using the microwave, water heater, and tv i would move ahead with the project.  I am thinking of installing a Marinco male connector in the side of the PC similar to the PC installed 30 amp male connector but would be designed to connect a 15 amp cord.  This would require drilling a 1 7/8” inch in the fiberglass exterior.  Anyone else drilled or cut the side panel and if so what was your experience?  I know Phoenix must successfully cut holes to install various electrical and plumbing ports but it makes me a little nervous.
Title: Re: 15 Amp Service Connection
Post by: jatrax on December 04, 2017, 09:07:37 pm
Quote
Am I correct in thinking that campground outlets with 15 amp and 30 amp service are capable of supplying a total of 45 amps or would they typically be protected at a maximum of 30 amps?
@fandj, in a perfect world you might be correct.  However, I suspect the answer to that question is "probably not".  While it is certainly possible that some parks are wired that way I think most would just run the wire to the 30 amp receptacle and tap off that to power the 15 amp one.  That means you are going to be restricted by the breaker in the pedestal, so 30 amps total.

The biggest problem is going to be we have no way to know how it was wired and in many different parks the wiring might have been done long ago or by folks not necessarily concerned about the NEC book.  Certainly it would be significantly cheaper to tap a 15 amp receptacle off the 30 amp wire rather than add another breaker in the main and run another set of 12/3 out to each pedestal.  And often cheap wins regardless of code.

Title: Re: 15 Amp Service Connection
Post by: ron-n-toni on December 05, 2017, 08:08:13 am
Hey, I like that idea. We have a 2017 2552. and have the same problem. If the home run circuit is installed as you say, in a workmanship manner, why not. I have watched people change out the front panels of the pedestal and it appears to me that the thirty and twenty amp outlets are just 'LEGS" off the 240 volt line. I have in the past gone out in the colder weather and had a heat tape wrapped around the sewer system on my previous 2351 and plugged it into the twenty amp outlet while the camper was plugged into the thirty amp and works just fine. But as Fanji says, depends on the pedestal (exactly)
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 05, 2017, 09:12:04 am
I agree with jatrax.  Each campground power pedestal could be wired differently.  At the same time, if the power pole is not shared with an adjacent neighbor, use both 30 amp outlets, and use a 30-to-15 amp adapter for the 15 amp power cord for your space heater  It seems easy enough to run a separate 14/3 extension cord from the power pole to your electric space heater inside your PC.  Just make sure not to pinch the cord when closing your van door.  Find the best location in the door jamb that has the least pressure against the extension cord.  Maybe you could tape a short wood dowel rod of the same diameter of the cord, to the cord when closing the door to relieve any pinching of the cord.
Title: Re: 15 Amp Service Connection
Post by: jatrax on December 05, 2017, 10:42:21 am
Quote
If I can get comfortable that this is safe and indeed will provide me the ability to run the portable heater while using the microwave, water heater, and tv i would move ahead with the project.
Provided the additional receptacle is the only thing powered by the added 15 amp input and therefore has no other connection to the rig I see no safety issues.  So assuming the the pedestal is wired to allow more than 30 amps it should work.  And if it wasn't wired to handle that then the breaker should trip. 

I am always leery of electrical systems I did not personally have a hand in.  One of the foundations of our safe electrical system in this country is that everyone follow the 'rules' which is the NEC book.  So I am trusting that the electrician before me wired things correctly.  Sadly I have been in numerous situations where that was NOT the case and have gotten zapped more than once because someone did something not to code.

I always use an electrical tester on the pedestal before plugging the rig in, just to check. 

Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 05, 2017, 04:05:19 pm
 Find the best location in the door jamb that has the least pressure against the extension cord.  Maybe you could tape a short wood dowel rod of the same diameter of the cord, to the cord when closing the door to relieve any pinching of the cord.

Indeed, find the best location. In our 2350, the lower rear corner of the door is the best spot I found. Plenty of 'cush for the push' and the door flexes easily there. We have the RV on 30A shore power in the driveway for the coach power, and have a 12ga cord running out to run a dehumidifier as we sort out water leaks.  pyho 

I would not think a dowel would help in this respect, maybe would in others. When in doubt, follow Ron.  2o2

As far as sorting out whether the 'legs' on a 20A/30A circuit are shared on a post, use a multimeter. if you get 220V 'hot to hot' 20 to 30, they are different legs. 0V they are 'shared'


Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 05, 2017, 04:35:47 pm
....and have a 12ga cord running out to run a dehumidifier as we sort out water leaks.  pyho
Where is rain water showing up in your PC?  I ask because some time ago I read a few other people experiencing water leaks near the entry door.  The culprit was the electric awning, specifically where the wires pass through from inside to outside to supply power to the drive motor.  Others had water coming in through the slide out.  I don't recall the exact resolution.  What I do recall was that the solution confused me.  Since neither applied to me personally, I didn't give either enough brain power.  Maybe others can help you through the trouble-shooting process.
Title: Re: 15 Amp Service Connection
Post by: Joe R on December 05, 2017, 07:26:44 pm
Fandj, picture the pedestal plug in like your breaker panel at home. Most common in houses are 100 or 200 services. So the power company would run wire that would support your maximum panel amperage.
Now your breaker panel has a main breaker that feeds a buss bar that all the other breakers connect to. So the service wire going to your house is the same as the under ground wire going to the pedestals in the campground. All the pedestals I have used have separate 30 and 15 amp breakers. Any campground that would wire a 15 amp receptacle into a 30amp breaker is asking for a lawsuit if an accident ever happened.   If the pedestal has a 30 amp plug and breaker, and a 15 or 20 amp plug and breaker you can draw a total of 45 or 50 amps from the 2 plugs.
I would suggest that you use 20amp outlet and 12 wire inside the PC. at 1500 watts and 120 volts that equals 12.5 amps. If the voltage drops to 110 volts the amperage jumps to 13.6. at this amperage for extended time, will over heat a 15amp breaker and it will trip. And I would use 10 wire for your extension cord because there would be less resistance than a store bought 14 gage wire.
Title: Re: 15 Amp Service Connection
Post by: jimmer on December 06, 2017, 10:11:42 am
Fandj,  pretty sure I saw on this forum, or another,  maybe RV.NET,    where someone had drilled through the exterior wall in the dinette area to accomplish running an extension cord to the pedestal 15/20 amp outlet.      Using a rubber 'plug'  to  cover the hole when not in use.    According to him,  it worked out very well.    Obviously had to be very careful on placement of the hole.
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 06, 2017, 08:06:13 pm
Any campground that would wire a 15 amp receptacle into a 30amp breaker is asking for a lawsuit if an accident ever happened.   


well, I dont see a big liability in it. My local RV shop sells this, and it would certainly give one a 15A outlet with a 30A breaker servicing it. They DO only rate it for  1875W @  125V , or 15A. I suppose it would let the magic smoke out of the wires if run higher..  roflol

http://www.campingworld.com/shopping/item/power-grip-adapter-30a-male-to-15a-female/27985

I think its just a matter of how the post was wired initially. *IF* there is 220V run to the post anyway, its an easy matter to have the 15A and 30A on different legs. But WHO KNOWS how it was wired, so the multimeter is the 'truth teller' here.  Should the post be originally wired for 110V 30A and the 15A outlet added, i would expect to find them both on the same leg. With a 30A breaker servicing them both.

( I dont have a current NEC book, and have never wired for RV use.  :-[ Might be a whole section there... but I have seen code ignored.  (nod) )

Title: Re: 15 Amp Service Connection
Post by: Joe R on December 07, 2017, 04:07:21 pm
I'm sure there are a lot people that use those adaptors with no issues. that rating would be in a perfect world, say the campground voltage is at 110 now it would be 17 amps. And if you use a extension cord sold in the big box stores. They are 16 gauge wire and there rating is 13 amps for 1625watts at 125 volts.
So now what happens if something goes wrong. You don't have a breaker anymore. You have a 25 or 50 foot (or what length cord your using) fuse that will burn in two before the breaker senses a need to trip, Except in a dead short.     
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 09, 2017, 01:46:13 pm
  I am thinking of installing a Marinco male connector in the side of the PC similar to the PC installed 30 amp male connector but would be designed to connect a 15 amp cord.  This would require drilling a 1 7/8” inch in the fiberglass exterior.  Anyone else drilled or cut the side panel and if so what was your experience?  I know Phoenix must successfully cut holes to install various electrical and plumbing ports but it makes me a little nervous.

I know the post got a bit off topic, but back to your original question.

Thinking about it, I may do this same modification to add the outlet like you describe. We are running a dehumidifier often, and I do not want a high draw appliance running unsupervised using the coach electrical. I can see running a space heater when parked also.

I have been running a cord in the drivers door. Works, but not the best solution.  :)

I would like to have the shore connections near each other, at least on the same side. Mrs Volkemon is in the camper now getting ready for tonight, so a more detailed inspection of the current shore power connector area inside must wait.

One option I like is putting it on the slide. I have the fold down couch, and there is a spot I could surface mount a box. Fairly well hidden, yet easy to get to slide in or out.

pro's-
1) correct side
2) no plumbing to hit
3) minimal low voltage wiring in the wall, only a 12V line to the overhead light. I can see it goes up the rear outside wall of the slider, so easy to avoid.

cons-
1)wire will be hanging out when slide extended
2)appearance of surface mounted box inside. I would prefer a wall mount.

 The wall seems pretty uniform when I press on it, so not so easy to locate the aluminum framing. :( if I stick to this location, I may drill a few small holes on the inside, down below the couch trim. If aluminum spirals come out... I hit one.  :-D  I am going to try a studfinder also, if I can find mine.  :lol

I will explore the area back by the other connectors some more. I would prefer all the connections together.  Mrs V just informed me that the top shelf below the sink is soaked..  pyho more leaks.

Below - good mounting location for the power box if I do choose the 'on the slide' option.

Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 09, 2017, 02:18:53 pm
I am concerned any 120V electric on a moving slide-out runs a risk of something going wrong via an over-sight, forgetting you have it plugged in somewhere.  A power cord inside or outside could get pinched or stretched or sheared off.

I would place the pictured pass-thru on a fixed exterior wall, maybe adjacent to the 30 amp if accessible.  An alternate location might be near your exterior fridge or furnace panels.  Maybe near the single battery compartment there....if you have the single battery.  Or does your 2006 have twin batteries by the main entry door, the same as later model years?  2006 was the transition year from one to two batteries.

On the inside,  I would wire a duplex outlet via Romex (or better) & junction box mounted near the floor in the area of your wall closet or fridge.  Make it all 20 amp because your 2006 has 20 amp, 12 gauge wire throughout.  Any owner mods should follow the same practice for the same reason....wire & termination over-load insurance.
(https://d1rnt4jswe7umx.cloudfront.net/images/products/thumb/3b9c6064bf38989913269b28e3a5a592.jpg)

Title: Re: 15 Amp Service Connection
Post by: donc13 on December 12, 2017, 04:41:02 pm
There is ONLY one way to do it safely... A 50 amp plug to 30a AND 15a adapter.

https://www.amazon.com/dp/B01MRN4C73/ref=asc_df_B01MRN4C735299883/?tag=hyprod-20&creative=395033&creativeASIN=B01MRN4C73&linkCode=df0&hvadid=198064502357&hvpos=1o2&hvnetw=g&hvrand=5556998667899434989&hvpone=&hvptwo=&hvqmt=&hvdev=m&hvdvcmdl=&hvlocint=&hvlocphy=9028903&hvtargid=pla-348585281213

Which means you MUST select a spot with a 50a receptacle.

Your other option... Turn off the heater before you use the microwave.
Title: Re: 15 Amp Service Connection
Post by: Joseph on December 13, 2017, 10:43:42 am
If your going to place a ground fault recepticle you have the issue someone mentioned of concerns of if something shorted such as your heater. Also I have yet to see a ped that the adjacent 15 amp 110 outlet wasn’t on its own breaker.

I have considered doing exactly what you are looking at and rather than drilling thru fiberglass I have considered having the connection just under fiberglass by adding a bracket to hold it there, much like your receptacle for your toad wiring in the rear. I would place it either near the battery box which might be a pain due to having to having to throw your cord under the rv at every hook up due to the ped being on the other side. If I do this I will place the ground fault on the cabinet near/under the sink as it allows easy access under neath. The issue here if you place the male exterior recepticle on the side of the ped is running your wiring to the passenger side before entering.  So once I get around to it if I can find a good way to run the supply wire from the ped side to the passenger side of the rig that will be my first choice. If not I’ll deal with throwing the cord under or dragging along a long enough cord to go around the rig to the ped.
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 13, 2017, 12:28:22 pm
There is ONLY one way to do it safely... A 50 amp plug to 30a AND 15a adapter.

https://www.amazon.com/dp/B01MRN4C73/ref=asc_df_B01MRN4C735299883/?tag=hyprod-20&creative=395033&creativeASIN=B01MRN4C73&linkCode=df0&hvadid=198064502357&hvpos=1o2&hvnetw=g&hvrand=5556998667899434989&hvpone=&hvptwo=&hvqmt=&hvdev=m&hvdvcmdl=&hvlocint=&hvlocphy=9028903&hvtargid=pla-348585281213


Which means you MUST select a spot with a 50a receptacle.

Your other option... Turn off the heater before you use the microwave.

The question posed by the OP was how to install the service connection in/on his RV. We have turned it into a discussion of electrical supply..  :lol  BUt indeed informational!

I am unclear as to how using the 30A and 15A outlets in a properly wired pedestal would be dangerous. Even if they were supplied off the same leg, each outlet has its own local breaker, and the 15A is required to have its own GFCI. A short circuit or overload condition on either outlet is protected by the correctly sized breaker in the pedestal.

The adapter you link to has no circuit breaker protection for the 30A or the 15A outlets. Each of these outlets would be protected by one leg of the 50A breaker in the pedestal. So now there is a 30A service protected by a 50A breaker, and a 15A service protected by another 50A breaker. This appears to be the most dangerous solution so far.  :beg   I welcome correction on this. Please.

Found a free online link to the 2011 NEC , and been studying section 551 which covers RV services.  It has helped a lot, as I have little (ok...NO  roflol ) experience wiring up RV park pedestals.

One piece of info I have yet to find is current required to melt a wire...
IE: I take a 14/3 cord, and wire nut the hot and neutral together.  :-[    IF I run it on a 30A breaker, does it trip the breaker before the wire glows red hot and/or melts the copper? 50A breaker?

Some destructive testing might be in order. I have to imagine someone else has had to try this already... just cant find it.

Title: Re: 15 Amp Service Connection
Post by: donc13 on December 13, 2017, 07:20:56 pm
There is ONLY one way to do it safely... A 50 amp plug to 30a AND 15a adapter.

https://www.amazon.com/dp/B01MRN4C73/ref=asc_df_B01MRN4C735299883/?tag=hyprod-20&creative=395033&creativeASIN=B01MRN4C73&linkCode=df0&hvadid=198064502357&hvpos=1o2&hvnetw=g&hvrand=5556998667899434989&hvpone=&hvptwo=&hvqmt=&hvdev=m&hvdvcmdl=&hvlocint=&hvlocphy=9028903&hvtargid=pla-348585281213


Which means you MUST select a spot with a 50a receptacle.

Your other option... Turn off the heater before you use the microwave.

The question posed by the OP was how to install the service connection in/on his RV. We have turned it into a discussion of electrical supply..  :lol  BUt indeed informational!

I am unclear as to how using the 30A and 15A outlets in a properly wired pedestal would be dangerous. Even if they were supplied off the same leg, each outlet has its own local breaker, and the 15A is required to have its own GFCI. A short circuit or overload condition on either outlet is protected by the correctly sized breaker in the pedestal.

The adapter you link to has no circuit breaker protection for the 30A or the 15A outlets. Each of these outlets would be protected by one leg of the 50A breaker in the pedestal. So now there is a 30A service protected by a 50A breaker, and a 15A service protected by another 50A breaker. This appears to be the most dangerous solution so far.  :beg   I welcome correction on this. Please.

Found a free online link to the 2011 NEC , and been studying section 551 which covers RV services.  It has helped a lot, as I have little (ok...NO  roflol ) experience wiring up RV park pedestals.

One piece of info I have yet to find is current required to melt a wire...
IE: I take a 14/3 cord, and wire nut the hot and neutral together.  :-[    IF I run it on a 30A breaker, does it trip the breaker before the wire glows red hot and/or melts the copper? 50A breaker?

Some destructive testing might be in order. I have to imagine someone else has had to try this already... just cant find it.



A 50 amp receptacle on a pedestal is 220 (240) volts.  Just like the wiring coming into your house... Two separate 120v circuits but they are 180 degrees out of phase so between the 2 circuits you get 240 volts.   Each one has a 50a breaker and they are tied together so if either line exceeds 50a, both sides will open (via the breaker).

However, the adapter I showed separates those 2 sides into a 30a socket and a 15 (20) amp socket.  Correct, there are no breakers in that adapter, but your 30a shoreline DOES have a 30a breaker for the shoreline.  One would presume that if you are going to put a 20 amp shoreline hookup in the fiberglass, you'd also put a 15 or 20a breaker between it and the receptacle where you'd plug in the heater.

That ONE receptacle would ONLY be hot when you ran the 2nd shoreline.   Without that 2nd shoreline plugged in, the receptacle would not be powered.

Using the adapter will guarantee that the 30a and 15a lines don't come off a single 30a breaker.

I have seen many RV park pedestals where there is only a 30a and 50a breaker but 3 receptacles.. 50a, 30a and 15a.

See attached pdf
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 14, 2017, 06:53:24 am


A 50 amp receptacle on a pedestal is 220 (240) volts.  Just like the wiring coming into your house... Two separate 120v circuits but they are 180 degrees out of phase so between the 2 circuits you get 240 volts.   Each one has a 50a breaker and they are tied together so if either line exceeds 50a, both sides will open (via the breaker).

That has not been my experience. When one leg of a 220V service is used as a 110V source, only that 1/2 of the breaker trips. The bar between the two legs on the breaker many times allows one leg to trip and not the other. 

However, the adapter I showed separates those 2 sides into a 30a socket and a 15 (20) amp socket.  Correct, there are no breakers in that adapter, but your 30a shoreline DOES have a 30a breaker for the shoreline.  One would presume that if you are going to put a 20 amp shoreline hookup in the fiberglass, you'd also put a 15 or 20a breaker between it and the receptacle where you'd plug in the heater.

Correct, but the wiring between the pedestal and the coach breaker box are rated for 30A and 15A. The only protection between the post and the breaker box in the coach comes from the breakers in the pedestal. So should a short appear between the pedestal and the coach, say in your shore power connector, the pedestal breakers will trip. 
With the adapter, the 'proper' 30A and 15A shore power connector cables/wiring are now not protected by the proper size breaker. The circuits in the coach 'downstream' of the coaches breaker box are indeed protected. The shore power cables outside, and the wiring inside the coach from the shore power receptacle and into the breaker box are now not protected properly.


That ONE receptacle would ONLY be hot when you ran the 2nd shoreline.   Without that 2nd shoreline plugged in, the receptacle would not be powered.

Agreed 100%

Using the adapter will guarantee that the 30a and 15a lines don't come off a single 30a breaker.

Also true, but it having both on one 30A breaker will err on the side of safety. The 30A service between the pedestal and the coach breaker box will be properly protected, the 15A will be 'underprotected' because it will need to draw 30A + to trip the breaker if no power is being used from the 30A outlet. Both cables are limited to 3600W total power (at 120V).
With the adapter in a 50A outlet, the 30A side and/or the 15A side will need to draw 50A+ to trip the pedestal breaker. 6000W per cable (50A x 120V) or 12,000W total for both cables at 120V. Over three times the energy available to heat things up. 


I have seen many RV park pedestals where there is only a 30a and 50a breaker but 3 receptacles.. 50a, 30a and 15a.

I have gotten a few stares over this week hopping out of my VW Bus to inspect pedestals around here. After looking at ~15 or so, I also have noticed the 30A always has a 30A breaker, maybe 1/2 have the 20A breaker (I assume) feeds the 20A GFCI in the pedestal. The others just have a GFCI outlet protected by the 30A breaker. The 50A always have a 220V 50A breaker.
I know from residential wiring that things are NOT always wired 'to code'. Thats why I preface things with 'properly wired' if stating an example case.





It is indeed a luxury to be able to discuss and find potential problems like this here at the desk, rather than finding them while camping. Thank You! 

I am starting to understand why I see so many references to 'illegal' adapters on RV forums.  Having a 15A cord with the breaker built into the male end seems like a VERY good purchase. Like one of these, but maybe with a cord longer than 6 foot.  https://www.amazon.com/Power-All-Extension-Moisture-Resistant/dp/B00CJI9XMC/ref=pd_lpo_sbs_86_t_1?_encoding=UTF8&psc=1&refRID=NK50FNRSGP69SKPFYD49

I am not finding any 30A 110V cords with this same feature. If they are out there, I can see the same value in them.

Maybe there is a 'correct' adapter that takes the 50A 220V service, slits it to (2) separate 110V services, and adds breakers and female plugs. If I wasnt expected to be working, I would keep searching....  :lol   Thanks again!
Title: Re: 15 Amp Service Connection
Post by: fandj on December 14, 2017, 08:19:24 am
Volkemon thanks for the link on the power cord with breaker.  Do you know if the breaker is actuated on amps or ground fault or power surge?  I wasn’t able to find anything specific in the description or questions.

If it is a true current limiting type breaker I think I may buy it as another layer of protection.
Title: Re: 15 Amp Service Connection
Post by: Joseph on December 14, 2017, 11:04:56 am
Sure seems like it’s being over engineered. You could run a cord From the pedestal throw it thru a window and run your portable heater and be legal and safe. Not that anyone wants to do that but it is safe. What I’m getting at is you can add all these fail safes for this one 110 outlet and end up paranoid  the rest of the coach isn’t as safe.
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 14, 2017, 11:54:20 am
Sure seems like it’s being over engineered. You could run a cord From the pedestal throw it thru a window and run your portable heater and be legal and safe. Not that anyone wants to do that but it is safe. What I’m getting at is you can add all these fail safes for this one 110 outlet and end up paranoid  the rest of the coach isn’t as safe.
Your thoughts are my thoughts with this one.

At the same time, I could see myself over-engineering this topic after one bad electrical mishap.  And it does seem like there are simple solutions we can easily implement via "protection inside the power cord".  It is nice to know there are such things available.  As someone had mentioned, it would seem ideal to have a 30A 30 foot power cord with circuit breaker protection built into the head of it, as found with the 15A cord with circuit protection.  That way you need not rely on the operational condition of the circuit breaker inside the power peg.

I quickly found the Power-All brand cords on Ebay with free shipping.

14 Amp, 6 foot length for $12.08 with free shipping
https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-6-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161788?hash=item3627a1fe3c:g:QyMAAOSwNWxaLbct (https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-6-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161788?hash=item3627a1fe3c:g:QyMAAOSwNWxaLbct)

14 Amp, 15 foot length for $16.73 with free shipping
https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-15-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161702?hash=item3627a1fde6:g:QD8AAOSwi0xaLbco (https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-15-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161702?hash=item3627a1fde6:g:QD8AAOSwi0xaLbco)

14 Amp, 50 foot length for $31.61 with free shipping
https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-50-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161513?hash=item3627a1fd29:g:bOUAAOSwVNxaLbcb (https://www.ebay.com/itm/Power-All-Commercial-Grade-125-Volt-50-ft-Cord-w-Circuit-Breaker-14-Gauge/232593161513?hash=item3627a1fd29:g:bOUAAOSwVNxaLbcb)

Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 14, 2017, 12:09:32 pm
Sure seems like it’s being over engineered. You could run a cord From the pedestal throw it thru a window and run your portable heater and be legal and safe. Not that anyone wants to do that but it is safe. What I’m getting at is you can add all these fail safes for this one 110 outlet and end up paranoid  the rest of the coach isn’t as safe.

Well, this is the time to 'over engineer' - before one actually builds it.  :-D  Beats over engineering after the fire.  :)

Per your example above, say I do run the cord through a window, and plug in the heater.  Now I have a window that doesnt close all the way, letting out more heat. I also have lost the water/snow blocking purpose of the window, as I have to leave it open now. (I do plan on adding window awnings, as I like to have the windows open in the rain) Even with the awnings, the bugs will go in the opening also. I can see the value in a proper 'bulkhead fitting' to bring the power into the coach. Looks classy too.  ;)

Adding the 'fail safes' are actually to relieve the paranoia that the coach isnt protected due to bypassing/misuse of safety devices. Having that breaker at the male end of the 15/20A cord ensures *anything* downstream is protected. Likewise for the 30A. Even using an adapter that allows 50amps to pass through a 15A outlet will be made safe like that. If the park handyman was having a bad day with a weak breaker tripping, so bypasses it 'temporarily'... and forgets.. this will protect my coach.

Is ANYTHING fail safe and sure? Nope. But I find preparation and planning do go a long ways towards prevention.

 
Volkemon thanks for the link on the power cord with breaker.  Do you know if the breaker is actuated on amps or ground fault or power surge?  I wasn’t able to find anything specific in the description or questions.

If it is a true current limiting type breaker I think I may buy it as another layer of protection.


On lunch break now, so a little time to research...and WOW is it vauge about how the breaker works.  >(  Looked at several others, and they often state GFCI protection...but no mention of overcurrent protection.

Power surge would not be covered by this type of adapter, I am guessing. If it was, 'SURGE PROTECTION' would be all over it.  Its sad they dont list the type of breaker on this cord. Found the same product for sale in many other places, none specify GFCI protection, overcurrent, etc. Just 'Breaker' . I will research more, and be back.
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 14, 2017, 12:16:35 pm

..... And it does seem like there are simple solutions we can easily implement via "protection inside the power cord".  It is nice to know there are such things available.  As someone had mentioned, it would seem ideal to have a 30A 30 foot power cord with circuit breaker protection built into the head of it, as found with the 15A cord with circuit protection.  That way you need not rely on the operational condition of the circuit breaker inside the power peg.





Darn it... I was hoping you already had a source for the 30A cords Ron.  :)  It seems so simple...have a 30A breaker in the head of the cord, everything downstream protected. Must be some other details in implementing such a device that makes it not so common.

 
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 14, 2017, 12:28:53 pm
I wonder if there 15 and 30 Amp products available (a box thingy without a cord) that plugs into the power peg outlet, then you plug your cord into it.  It sounds silly to have redundant circuit breakers just inches apart, but it would assure reliable circuit breaker protection.
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 14, 2017, 12:37:00 pm
A quick search, I found this "indoor" 15 Amp box thingy.  I am not electrical savy....it says 15 Amp GFCI.  Is it just a GFCI or is it both a circuit breaker and a GFCI.  I don't think GFCI is the same as a circuit breaker.
https://www.zoro.com/power-first-plug-in-gfci-ylw-15a-5-15p-indoor-120va-5yl43/i/G1353143/ (https://www.zoro.com/power-first-plug-in-gfci-ylw-15a-5-15p-indoor-120va-5yl43/i/G1353143/)
Plug-In GFCI, Cord Length No Cord, Color Yellow, 15 Amps, NEMA Plug Configuration 5-15P, NEMA Receptacle Configuration 5-15R, Enclosure Rating Indoor, Outlet Configuration 1 Outlet, NEC Cord Designation No Cord, Range of Lengths No Cord, Voltage Rating 120VAC, 60 Hz, Number of Poles 2, Number of Wires 3, Material Durable, Heavy Duty Plastic, Reset Type Manual, Standards UL, CSA, Self-Testing No
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 14, 2017, 01:31:26 pm
Thats just a GFCI protector.

Southwire has a line of RV surge and GFCI protectors. https://rvpower.southwire.com/products/surge-protection/

Just got off the phone with their tech department, and NONE of their products have overcurrent protection. Just over/under voltage, surge and GFCI protection.

I asked if they had any overcurrent protectors for RV... nope. He said there is a breaker in the post for that.  2o2 I asked about possibilities that the post may be miswired, breaker bypassed, adapter used etc... got told that if any of those conditions exist, turn off the power and contact park management. And the adapters are not to be used, and should be illegal.  :lol In their world, overcurrent protection for an RV beyond what the pedestal provides is unnecessary and redundant. 

I respectfully disagree. For what thats worth.

I wonder if there 15 and 30 Amp products available (a box thingy without a cord) that plugs into the power peg outlet, then you plug your cord into it.  It sounds silly to have redundant circuit breakers just inches apart, but it would assure reliable circuit breaker protection.

I have no problems with redundant safety systems.

I wouldn't mind a box thingy with a cord.

 Cover to guard against the elements.
 Multiple inputs (50A 220V, 30A 110V, 20A 110V)  to source power from the pedestal.
  30A 110V breaker and a 20A 110V breaker feeding their respective outlets.

As usual, if I cant buy it, I will build it. This thread has been MOST helpful in realizing different power 'threat' scenarios. 
Title: Re: 15 Amp Service Connection
Post by: fandj on December 14, 2017, 02:38:48 pm
I kind of like the idea of belts and suspenders particularly after seeing the exterior condition of some power pedestals outlets as well as finding one that had a live improperly wired outlet.  15 amp residential style breakers are relatively cheap (<$10) but I have not found a small single breaker enclosure. Are these available?

I may have to rely on the 15 amp pedestal breaker but would rather not.  One normally depends on the 30 amp pedestal breaker for the power cord, internal PC wiring/connectors to the relay switch and to my power management system and finally wiring/connectors to the PC breaker box so perhaps this 15 amp circuit is not so different.  However, I would feel better with a belt as a backup to my suspenders.



Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 15, 2017, 09:55:49 am
 However, I would feel better with a belt as a backup to my suspenders.

 (exactly)  I have never heard this before, but LOVE it!

Found these breakers, other web images show the back better. two screw to mount to top, and you can just see the rear mounting screws for the power wires.

(https://newcontent.westmarine.com/content/images/catalog/large/2412369_LRG.jpg)

You can select 2.5A to 50A single pole on this page. Might be available elsewhere, I just found them here first.
blue-sea-systems--a-series-single-pole-white-toggle-circuit-breakers--P002413698


A good start. :) 






Title: Re: 15 Amp Service Connection
Post by: donc13 on December 17, 2017, 08:56:39 pm
 However, I would feel better with a belt as a backup to my suspenders.

 (exactly)  I have never heard this before, but LOVE it!

Found these breakers, other web images show the back better. two screw to mount to top, and you can just see the rear mounting screws for the power wires.

(https://newcontent.westmarine.com/content/images/catalog/large/2412369_LRG.jpg)

You can select 2.5A to 50A single pole on this page. Might be available elsewhere, I just found them here first.
blue-sea-systems--a-series-single-pole-white-toggle-circuit-breakers--P002413698


A good start. :) 








Not really.  That breaker is designed to be inside a circuit oanel box that is NOT exposed to the elements.

Your 30a shoreline is routed through the transfer s
Switch to your circuit breaker panel where BEFORE anything else, it goes thru a 30a breaker.

Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 18, 2017, 06:12:20 am


Not really.  That breaker is designed to be inside a circuit oanel box that is NOT exposed to the elements.




LOL... maybe we build things differently... but I was planning on this being inside a weather resistant box, outside. After the 50A male plug, but before the 30A and 15A female sockets.

Quote
Your 30a shoreline is routed through the transfer s
Switch to your circuit breaker panel where BEFORE anything else, it goes thru a 30a breaker.



I have not dug into the wiring between the shore power hookup on the outside of the coach and the breaker panel. I am overdue there. I am under the impression that my 30A shorepower plugs into the pedestal, or adapter(s) attached to it.

Then it connects to the bulkhead/connector on the side of my camper. Inside, there is wiring that connects the bulkhead to the transfer switch. From the transfer switch, there is wiring leading to the breaker box in the coach. In this box is a 30A fuse that protects the wiring from the pedestal to the coach from damaging short circuits after the breaker box.

So if I am using the 50A to 30A /15A adapter, with my 30A shorepower plugged in, dont I have to have 50A (or ~6000W ) of draw before the pedestal breaker blows? HOPEFULLY having the breaker putting near twice the power in before tripping does not leave me with hot wire fire before it blows, as the wiring and equipment before the coach breaker box is designed for a 30A.

This is truly a 'belt and suspenders' scenario. If there was a HUGE problem with this, there would be many more electrical fires reported in RV's. The adapters would be banned. There is not, and they are not.

The important thing however, is that I feel MY coach is protected. And others may have the same feeling.

Imagine if you will... the adapter below -
(https://images-na.ssl-images-amazon.com/images/I/71cG5bCy5kL._SX425_.jpg)

But with small (2x4x2) accessible boxes inline with the 30 and 15 amp outlets.*  Inside each of the boxes are the appropriate breaker (15A or 30A) feeding that outlet. I am thinking small screw cover watertight boxes, as HOPEFULLY one doesnt need to reset the breakers on a regular basis.  :-D  This would be a simple and SAFE way to use a 50A adapter, and have a current protected 30A and 15A service from it.  The shore power cable, the outlet on the coach, the internal wiring, transfer switch and the supply line to the coach breaker box are now all protected properly by a 30A breaker, not a 50. The additional 15A, be it a 'cord through the window' or other configuration, is now protected by a 15A breaker, not a 50A breaker.


Aside from a minor weight gain of the adapter, I dont see a down side to this. I do see benefits.

The holiday season has me a bit slow on my projects right now, but I plan on getting the adapter, boxes and breakers soon.

As always, corrections welcome!! Please.

* Hm... maybe just one bigger box with both breakers. Might be easier to work with. As usual, at work thinking about camper projects.  roflol





 
 
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 18, 2017, 02:09:38 pm
Alrighty... almost done with work. Got the BOM (bill of materials) figured out.*

Description of the finished item:

Adapter that will take a 50A service and convert it to two services- (1) 30A 120V and (1) 20A 120V. Both services will be overcurrent protected with the appropriate breaker (30A or 20A) and with lightning/surge suppression on each service. Breakers, suppressors and  wiring to be enclosed in a IP-66 certified weatherproof box. Components alone add 37 oz to adapter weight, I am allowing another 8+ oz for connectors, fittings, etc. Targeting 3 pounds (48 oz) additional weight to the adapter (weight 2 pounds, or 32oz). This makes for an entire package weight of 5 pounds (60oz) or less.

I am unable to find specs (yet...) for what a 50A outlet will support for weight. Field testing on our 50A air compressor cord, I was able to put 10 pounds of downward force (VERY conservative estimate, but not measured) on the cable with no signs of plug movement and/or cord distress.

Cost of parts will be ~$200, with the adapter being the most expensive part ($60). The adapter might be superseded by component parts making up the same assembly.

The only thing missing to have this perfectly 'legal' at this point is GFCI protection for the 20A service. This could be provided by not using the adapter, make my own cords and use one of these with an end cut off for the 15/20 Amp plug.-

(https://encrypted-tbn2.gstatic.com/shopping?q=tbn:ANd9GcQGuNx-O1Vlk74eAcYB9Ws1nq7r7y1-YPOOPWk4DgKNE4VJMHQeHLjJGVraVfNFVgiqYcdN-UiX&usqp=CAc)

*LOL...  roflol  I dont even make it to the end of the post before changing ideas... but it is firming up, and looking like a good project. It does add ~3 pounds to the adapter, more if I use the GFCI, but the entire setup should weigh less than a six pack of beer. And provide a longer lasting sense of comfort.  :-D

Might have to add a few blinky lights... people LOVE LED's..

(http://www.bitrebels.com/wp-content/uploads/2011/03/Homer-Simpson-Yelling-Beer.jpg)

WOW... 12 glass bottle beers are 9+ pounds a six pack. Did not know.. thank you intermanet!



Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 20, 2017, 06:06:39 am
UPDATE - found it was cheaper to get separate cords than an adapter. And fits my needs better.

1) 50A 4 foot service cord - ~$20 https://www.amazon.com/Coleman-Cable-4-Foot-50-Amp-4-Wire/dp/B002RL9JAW
2) 30A female outlet - cannibalized off a 15A to 30A adapter, with the handle 'thingy' on the 30A. - ~$15  https://www.homedepot.com/p/Camco-12-in-Power-Grip-Dogbone-Electrical-Adapter-with-Easy-Grip-Handle-55165/205518971?cm_mmc=Shopping%7cTHD%7cG%7c0%7cG-Pro-PLA%7c&gclid=EAIaIQobChMI-8LjgrCY2AIViASRCh1zQQnYEAQYAiABEgJ51fD_BwE&gclsrc=aw.ds&dclid=CK62_oewmNgCFckOhgodox8N7A

3) 20 GFCI with female plug, cannibalized from this - ~$15 each after shipping. I bought 2 at this price- https://www.sportsmansguide.com/product/index/voltec-20-amp-in-line-12-3-gfci-adapter-with-locking-end?a=1898300

So... Saved $10 PLUS added a GFCI for the 20A. And have a 4 foot cord so weight isnt on the pedestal outlet. Might have a slightly higher weight for the assembly from GFCI and longer cord on the 50A. Still want it to fit in a small plastic 'shoe box' size storage...  :-D

Hopefully have all parts after the Christmas to new years vacation, and build will happen then.

Title: Re: 15 Amp Service Connection
Post by: donc13 on December 20, 2017, 04:49:39 pm


Not really.  That breaker is designed to be inside a circuit oanel box that is NOT exposed to the elements.




LOL... maybe we build things differently... but I was planning on this being inside a weather resistant box, outside. After the 50A male plug, but before the 30A and 15A female sockets.

Quote
Your 30a shoreline is routed through the transfer s
Switch to your circuit breaker panel where BEFORE anything else, it goes thru a 30a breaker.



I have not dug into the wiring between the shore power hookup on the outside of the coach and the breaker panel. I am overdue there. I am under the impression that my 30A shorepower plugs into the pedestal, or adapter(s) attached to it.

Then it connects to the bulkhead/connector on the side of my camper. Inside, there is wiring that connects the bulkhead to the transfer switch. From the transfer switch, there is wiring leading to the breaker box in the coach. In this box is a 30A fuse that protects the wiring from the pedestal to the coach from damaging short circuits after the breaker box.

So if I am using the 50A to 30A /15A adapter, with my 30A shorepower plugged in, dont I have to have 50A (or ~6000W ) of draw before the pedestal breaker blows? HOPEFULLY having the breaker putting near twice the power in before tripping does not leave me with hot wire fire before it blows, as the wiring and equipment before the coach breaker box is designed for a 30A.

This is truly a 'belt and suspenders' scenario. If there was a HUGE problem with this, there would be many more electrical fires reported in RV's. The adapters would be banned. There is not, and they are not.

The important thing however, is that I feel MY coach is protected. And others may have the same feeling.

Imagine if you will... the adapter below -
(https://images-na.ssl-images-amazon.com/images/I/71cG5bCy5kL._SX425_.jpg)

But with small (2x4x2) accessible boxes inline with the 30 and 15 amp outlets.*  Inside each of the boxes are the appropriate breaker (15A or 30A) feeding that outlet. I am thinking small screw cover watertight boxes, as HOPEFULLY one doesnt need to reset the breakers on a regular basis.  :-D  This would be a simple and SAFE way to use a 50A adapter, and have a current protected 30A and 15A service from it.  The shore power cable, the outlet on the coach, the internal wiring, transfer switch and the supply line to the coach breaker box are now all protected properly by a 30A breaker, not a 50. The additional 15A, be it a 'cord through the window' or other configuration, is now protected by a 15A breaker, not a 50A breaker.


Aside from a minor weight gain of the adapter, I dont see a down side to this. I do see benefits.

The holiday season has me a bit slow on my projects right now, but I plan on getting the adapter, boxes and breakers soon.

As always, corrections welcome!! Please.

* Hm... maybe just one bigger box with both breakers. Might be easier to work with. As usual, at work thinking about camper projects.  roflol





 
 

You are overengineering and overthinking.

Your easiest, cheapest route is to either turn off your heater or your water heater when you use the microwave.

There is no such thing as a waterproof circuit breaker box.

Look at your home... Whatever size your main breakers are, they are smaller that ANY breaker between the power company and your main breakers.    And I doubt if any of the line breakers are as high an amperage as your main breakers.   You don't worry about a 100a breaker feeding a 15a breaker do you.

It's certainly your RV, do to it what you want.  I am just offering advice.

Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 20, 2017, 04:56:36 pm
Your easiest, cheapest route is to either turn off your heater or your water heater when you use the microwave.
That is our practice as I am sure is the practice of most others.  It works!
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 20, 2017, 06:45:40 pm


You are overengineering and overthinking.

Yep. We have named it 'Belt and suspenders'  :lol

Your easiest, cheapest route is to either turn off your heater or your water heater when you use the microwave.
True. The word we were focusing on is 'safest'.

There is no such thing as a waterproof circuit breaker box.

TRULY waterproof? to depth? Not in my budget.  :-D
An I going for any ratings/certifications/ 'UL' type listing. No. Even the 50A to 30A adapter specs say "No Certifications or Listings"
source - https://www.homedepot.com/p/Connecticut-Electric-50-30-Amp-Outlet-Adapter-CESMAD5030/202714807?cm_mmc=Shopping%7cTHD%7cG%7c0%7cG-VF-PLA-D27E-Electrical%7c&gclid=CjwKCAiAsejRBRB3EiwAZft7sP9qzioS015yWpTfpjxO2JQtjnQ20EZg6N2brzR-tiBZqb-U8r4aIxoC2OIQAvD_BwE&gclsrc=aw.ds&dclid=CLGI0ZjimdgCFcl8wQods8AP9A

The box I sourced is rated 'IP-67'
 IP-67 is 'waterproof' for the purposes of my discussion. "" IP "" = "Ingress Protection" or "what gets in".  6 is "no" dust, and 7 is "Protected against the effects of immersion in water to depth between 15 cm and 1 meter" Water PROOF? No. Not necessary. At the point this box is even 1 foot (~.3M ) underwater, my biggest concerns will NOT be if the breakers are getting wet.

Source - http://www.resourcesupplyllc.com/PDFs/WhatDoesIP67Mean.pdf

 

Look at your home... Whatever size your main breakers are, they are smaller that ANY breaker between the power company and your main breakers. And I doubt if any of the line breakers are as high an amperage as your main breakers.    You don't worry about a 100a breaker feeding a 15a breaker do you.

No, but if you look earlier you will find advice in this thread to have a 50A breaker feeding a 15A cord.. and said cord fed through a window as some may do on a cold winter night..  with no breaker in between. This whole project is to add that protection, and now the GFCI also. An added benefit is that the 30A outlet will now be protected by a proper 30A breaker, not a 50A.
 Oh yeah..and lightning protection. I live in the lightning capitol of the US, within 'Lightning Alley'. We plan to have many in-state trips in our coach.


It's certainly your RV, do to it what you want.  I am just offering advice.

THANK YOU! For even taking the time to post. I am here seeking advice from people MUCH more versed in RV travel than I am.  2o2


Title: Re: 15 Amp Service Connection
Post by: donc13 on December 20, 2017, 09:24:27 pm
Ok, my last comment.  There is NO circuit breaker that will prevent lightning damage to your house's or your RV's wiring.

First, the electrons (electricity) in lightning move at the speed of light.  Circuit breakers are mechanically open or close the circuit so by the time your breaker opens the circuit, the electricity has already entered your wiring, found a ground and jumped to it.

Second, the lightning just jumped across about a mile of air (an insulator), do you really think a 1/2 air gap once the breaker opens is going to stop the lightning?

Nuff said.
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 21, 2017, 05:42:56 am
Ok, my last comment.  There is NO circuit breaker that will prevent lightning damage to your house's or your RV's wiring.

NOt a strike, but 'lightning damage' ? Home Depot seems to think differently.. ""Siemens
20 Amp 6.5 in. Whole House Surge Protected-Circuit Breaker"" source - https://www.homedepot.com/p/Siemens-20-Amp-6-5-in-Whole-House-Surge-Protected-Circuit-Breaker-QSA2020SPDP/202562776  But not really a good match for my project at all.   Thats why I am using lightning arresters. https://www.alliedelec.com/hvca-he300/70016352/  one on each leg.


First, the electrons (electricity) in lightning move at the speed of light.  Circuit breakers are mechanically open or close the circuit so by the time your breaker opens the circuit, the electricity has already entered your wiring, found a ground and jumped to it.

Good grief. You do have Google right?

1) Electrons move HOW fast? A calculation shows that the electron is traveling at about 2,200 kilometers per second. That's less than 1% of the speed of light, but it's fast enough to get it around the Earth in just over 18 seconds.   Source - https://education.jlab.org/qa/electron_01.html

2) Maybe you meant the lightning flash.. The return stroke (the current that cause the visible flash) moves upward at a speed of about 320,000,000 ft per second or about 220,000,000 miles per hour (about 1/3 the speed of light). source - http://www.maine.gov/mema/prepare/prep_display.shtml?163524




Second, the lightning just jumped across about a mile of air (an insulator), do you really think a 1/2 air gap once the breaker opens is going to stop the lightning?

No. Nothing I am aware of will stop a direct lightning strike. Like WATERPROOF, nothing is truly LIGHTNINGPROOF.  Perhaps one  should consider the source of the majority of lightning strike damages are not the strike itself, but the surrounding effects. ""Lightning can strike the air conductors directly and surge voltages, even from kilometres away, can enter into your installation. This surge voltage is then passed to ground through your equipment which can lead to damage or complete destruction of your equipment.""  Little too much info to post here, but it is from South Africa, the Lightning Capital of the WORLD, not just the USA. Well worth reading. Source - http://www.clearline.co.za/how-lightning-affects-electronics


Nuff said.

Well,  thank you for the enlightenment.  I did learn a few things from your post, hope you did the same. Please do not hesitate to keep posting.

I may be 'overthinking' and 'over engineering' this project, but at least there is thought and engineering involved in my process.  ;)


The original poster has had the thread hi'jacked into a 'power supply' safety discussion, when the original question was 'ANYONE got advice on installing a 15A additional service on my RV?'  :lol  I am not at that point yet, but I do like the idea. But I want to improve the quality/safety of the supply going into my RV before I add a service like that.

Not trying to make the 'impenetrable shield' against lightning.

(http://www.motorhome.com/wp-content/uploads/2014/10/lightning-lead.jpg)

Not trying to make the supply waterproof in all instances.

(http://www.camillc.com/Site/images/terrawind/terrawind_water640.jpg)

and not wanting to spend $3oo-500+ for devices that do part of what I want.
(https://www.delcity.net/images/photos/225px/EMS-PT50X_primary_225px.jpg?v=20170915191327)
(This one is $450 with NO overcurrent protection.. NO GFCI on a 15A service.. https://www.delcity.net/store/50-Amp-EMS-Surge-Protector/p_823165.h_823166.r_IF1003?mkwid=s8dIRItUM&crid=38094426869&mp_kw=&mp_mt=&gclid=CjwKCAiA1O3RBRBHEiwAq5fD_AiM3beWviyjfqmzL6XKNbjVdBoDNV1K3T--y9ox8aRSmJOH2Vl11RoC0UgQAvD_BwE )


What I am trying to do is show others how they can make their own, along with some inspiration on how to think it out. Or show this to their friend who can build one for them. Maybe to reveal others that give 'advice' that sounds good, but does not stand up to closer analysis. Or to let others that know FAR more than me have a good laugh. Thats OK too. Hopefully when they regain their composure, they will post and show me what a fool I am. Wont be the first time.  (nod)

But as it stands, I think I am on track to have a product in my RV that can take a 50A service, and split it into a 30A and 15A service, with reasonable lightning/surge protection, overcurrent protection properly sized for each outlet, GFCI protection on the 15A as it should be, etc. All for ~ $250 and less weight than a 6 pack of Bud beer in bottles. (gonna be close)  More volume, but still aiming for 'in a shoebox' size or close.

THEN I intend to drill a hole and run some wires in the coach to answer the OP's question. Finally.  :-D




Title: Re: 15 Amp Service Connection
Post by: fandj on December 21, 2017, 12:38:08 pm
I wanted to post a follow up of what I have done at this point.

1.  I decided to purchase a Marinco male receptacle.  Not knowing for sure but suspected I may be overly brave or insane I decided to risk it and drill a 1 7/8” hole in the side of our relatively new motorhome.  I masked off the area the receptacle was to be installed and then bored a 1/8” pilot hole.  After this I reversed the rotation of the hole saw and proceeded slowly to drill the 1 7/8” hole.  Fortunately this was easily accomplished with no chipping of the exterior finish.

2.  I then installed the Marinco receptacle and sealed it with Eternabond Microsealant.  I used 2” long stainless bolts, fender washers, and nuts to secure the receptacle in place.  This is the second time using the Eternabond material and I am quite impressed with its sealing ability.

3.  12/3 cable was used to run to a dedicated GFCI outlet.  My outdoor cord to be used between the 15 amp campground pedestal is also 12/3.  Testing the new 15 amp service connection at home and with the 1500 watt electric space heater connected to the outlet it is pulling about 13.5 amps (measured by a Kill A Watt plugin meter).  This is within the capacity of the various components.

4.  Before starting this project I wasn’t sure the thickness of the various wall layers but after
retrieving the core I took some measurements for future reference.  In case someone ever needs similar information, on our PC the overall thickness is about 1 3/8” . The outer fiberglass skin is about 1/16”.  The skin is bonded to 1/8” plywood which is bonded to about 1” of styrofoam.  The interior plywood and paper like material completes the wall composite.

It appears this supplemental power arrangement along with the existing 30 amp service will allow the use of two 1500 watt space heaters along with the microwave and/or hot water heater.  Once I am able to test this out at various campgrounds I will provide a further update.
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on December 21, 2017, 03:51:21 pm
Looks good there fandj, like Phoenix did it for you.
Title: Re: 15 Amp Service Connection
Post by: jatrax on December 21, 2017, 04:14:24 pm
Thanks for posting that Fandj, especially the photos.  Looks like a nice neat job.
Title: Re: 15 Amp Service Connection
Post by: Volkemon on December 22, 2017, 06:25:35 am
Looks Great!  Wish I had a wide open space like that on the 2350. I have been exploring adding it by the existing 30A, but forward there is wheelwell, and rearward is bathroom. Yours looks 'factory'.  2o2

Thanks for the pic's also. especially the 'core section'
Title: Re: 15 Amp Service Connection
Post by: ron-n-toni on December 22, 2017, 08:58:34 am
Now all you need is some nice cold weather with a little snow/sleet and a place to plug it in. It has been interesting reading tho.
Title: Re: 15 Amp Service Connection
Post by: fandj on January 14, 2018, 08:30:17 am
I wanted to report back after actually putting the supplemental power connection to use.  While camping in 39 degree weather I connected a 1500 watt heater to the new dedicated  outlet (connected separately to the 20 amp pedestal outlet) in the sleeping area and another 1500 watt heater just behind the drivers seat (PC standard supplied outlet).  The rear heater pulled about 13 amps whereas the front heater along with the refrigerator, hot water heater, lights, etc. at times pulled about 24 amps for a combined total of about 37 amps.  All wiring and connectors were cool.

The ability to run two heaters simultaneously provided for more even temperatures between the front and rear of the coach without concern of tripping a breaker which was the original goal.  For lower outside temperatures the second heater will no doubt provide more comfortable and uniform inside temperatures.
Title: Re: 15 Amp Service Connection
Post by: Ron Dittmer on January 14, 2018, 09:58:49 am
Good For You fandj!  That is a great mod, "proven" itself to be of great value.